3V output on SV switch

So I have a gas fireplace control module that runs off of a 3V AC power supply, if I power my SV switch from a separate DC power adaptor can I run 3V AC output on isolated mode? Or does the switch input voltage always match the output?
1 Comment

Hi Michael, in order to manage a diferent tension on the output of the SV you will need to isolate the relay from the input removing (desoldering) a couple of SMD zero ohm resistors. See the "isolated mode" section here;

https://ewelink.coolkit.cc/?p=151

Regards,
Mario.