Hello can you tell me if a 150watt light bulb 240v will be ok for the Sonoff Basic

thanks


So I just these sonoff basics from Amazon. Box says basic, board says RF , the main traces have been replaced by wires, it's using an esp 8285 and I think I see a fuse. Did sonoff completely change their manufacturing or is this a knock off?

15 x 15W = 225VA / Voltage = Amperage.  So if your line voltage is 120 the 15 lights require a total of  1.875 Amps.


For an inductive load like LED transformers I would keep the Sonoff basic load under 7A to protect the relay contacts.

i have 15 watts led panel light total 15 pcs


Then you have an inductive load of 225VA.  Divide 225 by your voltage to get amperage.


For inductive loads I would probably try to stay below 7 amps.  Inductive loads put more strain on the relay contacts.

"15 watts led panel light total 15 pcs"


15W * 15 = 225W or 225VA


For 120V circuit:   225VA / 120V =  1.875A


For 240V circuit:   225VA / 240V =  0.938A


The Sonoff  basic is rated at 10A into a resistive load.  If you are pulling a heavily inductive load like a LED or CFL transformers or ballasts I would derate it by 30% to get the expected life out of the relay contacts.  For that type load 7A or less should be okay.

150VA / 240V =  0.625A   The basic is rated at 10A  so yes, it will handle it easily.


1 person likes this

i have 15 watts led panel light total 15 pcs ....can it be connected in single sonooff basic .....or required 15 pcs each ...trhanks 